Per NFPA #20 Table 2-20 Summary of Fire Pump Data the minimu suction and discharge for a 1,500 gpm booster pump is 8".
Of course we all understand that is the minimum allowable size and it often happens site conditions dictate a larger, usually on the suction side, size be used.
Backflow preventors I believe an are excellent example.
Take a look at a snapshot taken from Ames for the 3000ss double check.
For an 8" 3000ss the "Rated Flow" is 1,600 gpm but beside that is the point where UL tested and the test appears to run out to about 2,350 gpm.
I've always worked under the assumption I can use this only where my required flows do not exceed the maximum rated flow or 1,650 gpm. To me this is not unlike fire pump test curves which exceed 150% of rated capacity. The factory may very well test a 1,500 gpm pump to 2,500 gpm and supply the certified curve but that doesn't mean I can use that curve to design a system requiring 2,300 gpm.
In the case of this particular 8" Ames am I correct in saying this particular backflow preventor would not be acceptable on a system requiring more than 1,650 gpm?
Then there is the fire pump itself.
Here in Georgia the state requires all fire pumps to be able to operate to 150% without drawing any portion of the suction below 20 psi and they are starting to require it be demonstrated on fire pump tests.
I'm not sure but I think this is a requirement everywhere throught the EPA... something to do with the clean water act of a long time ago but not so sure of that.
Anyway, am I right in my way of thinking?
Thanks.
Of course we all understand that is the minimum allowable size and it often happens site conditions dictate a larger, usually on the suction side, size be used.
Backflow preventors I believe an are excellent example.
Take a look at a snapshot taken from Ames for the 3000ss double check.
For an 8" 3000ss the "Rated Flow" is 1,600 gpm but beside that is the point where UL tested and the test appears to run out to about 2,350 gpm.
I've always worked under the assumption I can use this only where my required flows do not exceed the maximum rated flow or 1,650 gpm. To me this is not unlike fire pump test curves which exceed 150% of rated capacity. The factory may very well test a 1,500 gpm pump to 2,500 gpm and supply the certified curve but that doesn't mean I can use that curve to design a system requiring 2,300 gpm.
In the case of this particular 8" Ames am I correct in saying this particular backflow preventor would not be acceptable on a system requiring more than 1,650 gpm?
Then there is the fire pump itself.
Here in Georgia the state requires all fire pumps to be able to operate to 150% without drawing any portion of the suction below 20 psi and they are starting to require it be demonstrated on fire pump tests.
I'm not sure but I think this is a requirement everywhere throught the EPA... something to do with the clean water act of a long time ago but not so sure of that.
Anyway, am I right in my way of thinking?
Thanks.