By Banded in both directions, I mean a proper 2 way distribution with distributed tendons in both directions loading bands in both directions.
Basically 50% of the load is carried in each direction by the distributed tendons and these distributed tendons are then supported by banded tendons picking up the distributed tendon load and carrying it to the supports. Thus 100% is carried in each direction. But then, the 50% distributed in each direction can be modified as long as the respective bands are modified accordingly. So the distributed could be split 70/30 as long as the banded is split 30/70, still giving 100 in each direction.
The US one way banded distributed system is one extreme of this where the distributed % is 100/0 and the banded % is 0/100, thus still carrying all of the load in each direction.
100% banded tendons in both directions was proposed and used in Europe in the 70/80's (definitely in the Netherlands but possibly in other countries as well). In this case, the middle strip is reinforced with passive reinforcement. Costs more but easier installation. I was asking my questions of pappyirl to see if this was what he was suggesting.
Concrete slabs work the same way in all countries, simplistic (and sometimes dangerous) Code rules often limit people who know what they are doing from designing a slab in the best way possible. The rigid rule in ACI allowing banded/distributed or 75/25% distributions only is stupidly restrictive to designers who usderstand slab design (not simply how to apply some code rules).