Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

BAR SIZE LIMITATION FOR WATER RETAINING STRUCTURE

Status
Not open for further replies.

Tstruct

Structural
May 14, 2023
87
0
0
PK
I have heard that minimum #4 bar size must be used for water retaining structures. I searched in ACI 350 but didn't find any such clause. Can somebody please provide reference to any such clause if exists in ACI 350 or any other ACI code. For a small water tank retaining wall I am designing, #3 bar at 6" spacing is adequate. But there is debate for the bar size. Thanks, please comment.
 
Replies continue below

Recommended for you

ACI 350-06 7.12.2.2 requires #4 minimum bar size for shrinkage and temp reinforcement. That is pretty much everything IMO - main bars may not be controlled by temp and shrinkage but they are acting to resist it. Chapter 19 on shells and plate members requires #4 for everything (19.2.7). ACI 350 crack control provisions (as well as other codes) encourage use of smaller bar diameters with tighter spacings, as I am sure you know. What are you using for durability factor? The durability factor does take a hit when your working stresses are closer to strength design stresses in severe conditions (i.e. minimum load factor), so you may want to have some fat in there anyways...I would.






-Mac
 
Status
Not open for further replies.
Back
Top