Aakalim103

Structural
Jan 26, 2019
26
0
0
FI
I have a situation where we need a floor slab on top of a pile cap. Ideally, the pile cap can serve as a floor slab, but this would give us a very thick pile cap. So instead the manager is proposing a compacted gravel layer on top of the pile slab. The idea is to have a thinner base slab on gravel base in order to reduce the amount of concrete.

My question is that in such a situation, how would i go about designing the floor slab? The gravel will be compacted and laid over a fairly thick and rigid pile cap/mat. Should i use some subgrade reaction for the gravel or should i consider it rigid?

 
Replies continue below

Recommended for you



As far as I understand,the floor slab supported by partially pile cap but mostly by grade.. You may perform FEM and use softer springs for the span zone and hard springs on the pile cap zone..