I am trying to understand the failure of a standard 3 phase squirrel cage induction motor. This one is a Baldor
7.5 hp
1750 rpm
TEFC
213T frame
208/230-460 9 lead, connected low voltage per the motor diagram (2 parallel wye) Connections appeared to be secure, requiring the wire nuts and splices to be cut off with cutters to remove the cord at disassembly.
It's old as dirt and has recently begun slowing down under load and as part of the function of the machine is to blow material, the blower doesn't function adequately at lower rpm. As load cycle reduces, the motor speeds back up. this went on for several weeks and motor still runs though we have replaced it with another that does not show this variation in rpm which should eliminate the load as a primary cause of this problem.
Amperage was not over service factor amps, usually not over rated amps even while the motor was lugging
Voltage (at the motor plug, 1 foot cord) was 240 (good 3 phase present) while under load and lugging.
Can this be a rotor problem causing increased slip?
Rotor looks fine.
Windings (all 6 circuits)ohm good with equal resistance and coils appear undamaged (after cleaning)
Bearings are sealed ball though the motor has grease fittings installed, so as you might guess, the end bells were full of accumulated grease and some dust.
Never saw anything like this that didn't result in a burnout over the short term, this went on for several weeks running half hour out of every hour for several hours am and pm 7 days a week.
7.5 hp
1750 rpm
TEFC
213T frame
208/230-460 9 lead, connected low voltage per the motor diagram (2 parallel wye) Connections appeared to be secure, requiring the wire nuts and splices to be cut off with cutters to remove the cord at disassembly.
It's old as dirt and has recently begun slowing down under load and as part of the function of the machine is to blow material, the blower doesn't function adequately at lower rpm. As load cycle reduces, the motor speeds back up. this went on for several weeks and motor still runs though we have replaced it with another that does not show this variation in rpm which should eliminate the load as a primary cause of this problem.
Amperage was not over service factor amps, usually not over rated amps even while the motor was lugging
Voltage (at the motor plug, 1 foot cord) was 240 (good 3 phase present) while under load and lugging.
Can this be a rotor problem causing increased slip?
Rotor looks fine.
Windings (all 6 circuits)ohm good with equal resistance and coils appear undamaged (after cleaning)
Bearings are sealed ball though the motor has grease fittings installed, so as you might guess, the end bells were full of accumulated grease and some dust.
Never saw anything like this that didn't result in a burnout over the short term, this went on for several weeks running half hour out of every hour for several hours am and pm 7 days a week.