Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IDS on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Basis for when plants have evacuation buttons/break class or not..

Status
Not open for further replies.

jamesbanda

Chemical
Sep 21, 2004
223
I'm looking for guidenace or code references which cover requirements law or best pratice or otherwise...

I would assume flammable and toxic plants typically have these.. and this is what i've seen and it comes down to engineering judgement..

low hazard plants dont have these.. or low hazard plants on a low hazard site..

i'm confident i can design a suitable system for my project.. inline with what we have done elsewhere but i'd like to check if a standard exsits.

 
Replies continue below

Recommended for you

Hey James,

If it helps, I checked our own company standard titled "GENERAL SPECIFICATION FOR PLANT, FIRE AND GAS WARNING SYSTEMS" for references and there were very few, mainly NFPA 72 and 101 which you probably know. Apparently there is no specific API reference on this subject. Although our company standard lays everything out nicely for standards of installation like field emergency fire and gas alarm buttons, etc; the locations and need are stated to be determined by the facility owner. You would think there would be specific standards that insurance carriers would require for manufacturing sites, but I can't find any.

best wishes,
sshep
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor