Hi everyone,

i am facing problem in using Allen bradley compact logic system of the 1769-SM2 module, communicating with basler DECS-200. I wanted to read the data of holding register of 47275 - 47276. My basler Decs-200 address is 5. Therefore, the command message that i send was Device address = 5 , function code= 3 , staring register=7275 , number of register=2. However, the message block of the PLC is returning an error message of "Communication failure". Would appreciate any guidance from you guys. thanks
 
Replies continue below

Recommended for you

The message appears to be Modbus formatted message.

1) What is the physical comm link? 2 wire RS-485?

2) How is the CRC calculated? Is Modbus master a native implementation on CompactLogix so it calculates CRC? Or do you have a Modbus card and it calculates CRC? Or are you custom 'messaging' through some means?
 