One of the projects I'm working on:
A large crude tank was found to have a roughly 30'' wide band of corrosion on the interior of the top shell (~60' diameter). From inspection reports, it didn't look too bad so we just planned on putting lap patches as needed.
However, once the area was sandblasted it turns out that the corrosion was much more severe than expected. There are large areas of corrosion throughout this 'band' that would not meet the minimum thickness required to support the geodome.
API 653 has a maximum size of lap patches so I'm pretty sure we cannot just butt weld lap patches throughout the entire course of the shell. A partial solution to alleviate the compressive load of the geodome would be to add vertical stiffeners from the top windgirder (located on top course) to the intermediate windgirder. However, we are still looking for solutions regarding patching the areas of corrosion while staying compliant.
The solution must be cost and time effective..we cannot just replace the entire top shell course as we have business drivers, and the tank needs to be back in service by mid January.
Any thoughts?
One of the projects I'm working on:
A large crude tank was found to have a roughly 30'' wide band of corrosion on the interior of the top shell (~60' diameter). From inspection reports, it didn't look too bad so we just planned on putting lap patches as needed.
However, once the area was sandblasted it turns out that the corrosion was much more severe than expected. There are large areas of corrosion throughout this 'band' that would not meet the minimum thickness required to support the geodome.
API 653 has a maximum size of lap patches so I'm pretty sure we cannot just butt weld lap patches throughout the entire course of the shell. A partial solution to alleviate the compressive load of the geodome would be to add vertical stiffeners from the top windgirder (located on top course) to the intermediate windgirder. However, we are still looking for solutions regarding patching the areas of corrosion while staying compliant.
The solution must be cost and time effective..we cannot just replace the entire top shell course as we have business drivers, and the tank needs to be back in service by mid January.
Any thoughts?