kaspor
Electrical
- Aug 12, 2021
- 45
Hello
I am trying to wrap my head around how battery storage facility import/export power.
For these scenarios, assume grid voltage is 66kV, inverter output voltage is 660V, battery facility rated capacity is 20MVA, consisting of multiple inverters (for simplicity assume all inverters are equal in size and are lumped into one inverter).
For the import scenario, my understanding is as follows:
Inverters will decrease generated voltage angle amplitude to charge batteries or absorb reactive power up to the limits on the inverters PQ curve. Current will lead inverter voltage implying a leading power factor. On the limits of the PQ curve, a current will flow throughout the facility into the inverters and its imperative that these voltages are held within the inverters operating tolerance (e.g. +/- 10% 660V).
For the export scenario, my understanding is as follows:
Inverters will increase voltage angle/voltage amplitude to export real/reactive power into the grid up to the limits of the inverters PQ curve. Current will lag inverter voltage implying a lagging power factor. On the limits of the PQ curve, a current will flow throughout the facility into the grid. For this scenario, can you assume that the grid voltage will be held constant and if impedances within the facility (i.e. cables etc.) are too small, then the inverter will not be able to export at rated capacity? What happens in this situation? Is the inverter limited as to how much it can increase voltage angle/voltage amplitude?
p.s. apologies if I'm using the wrong terminology, by voltage angle I mean the phase angle difference between inverter generated voltage and grid voltage (I think some people call this load angle on a synchronous generator).
I am trying to wrap my head around how battery storage facility import/export power.
For these scenarios, assume grid voltage is 66kV, inverter output voltage is 660V, battery facility rated capacity is 20MVA, consisting of multiple inverters (for simplicity assume all inverters are equal in size and are lumped into one inverter).
For the import scenario, my understanding is as follows:
Inverters will decrease generated voltage angle amplitude to charge batteries or absorb reactive power up to the limits on the inverters PQ curve. Current will lead inverter voltage implying a leading power factor. On the limits of the PQ curve, a current will flow throughout the facility into the inverters and its imperative that these voltages are held within the inverters operating tolerance (e.g. +/- 10% 660V).
For the export scenario, my understanding is as follows:
Inverters will increase voltage angle/voltage amplitude to export real/reactive power into the grid up to the limits of the inverters PQ curve. Current will lag inverter voltage implying a lagging power factor. On the limits of the PQ curve, a current will flow throughout the facility into the grid. For this scenario, can you assume that the grid voltage will be held constant and if impedances within the facility (i.e. cables etc.) are too small, then the inverter will not be able to export at rated capacity? What happens in this situation? Is the inverter limited as to how much it can increase voltage angle/voltage amplitude?
p.s. apologies if I'm using the wrong terminology, by voltage angle I mean the phase angle difference between inverter generated voltage and grid voltage (I think some people call this load angle on a synchronous generator).