Hi guys,
I have been using the latest Earthquake loading code AS1170.4-2007 that requires a kp value based on the annual probability of exceedence that is referenced from either the BCA or AS1170.0 Table F, found in Admt 2-2003 and later revised in Admt 4-2005.
Now, the BCA has two values, for Importance Category (IC) 1,2 and 3 buildings an exceedence interval of 500 years is used and for IC4 buildings an exceedence interval of 800 years.
Conversly AS1170.0 further sub-divides the IC with design lifes and the exceedence intervals vary from 25 years for an IC1 building with a design life of 6 months, to 2500 years for a IC4 building with a design life of 50 years.
How have others been deriving there kp values when using AS1170.4-2007, are you using the exceedence intervals set-out in the BCA or AS1170.0 and why is there such a variation between the two documents.
I have been using the latest Earthquake loading code AS1170.4-2007 that requires a kp value based on the annual probability of exceedence that is referenced from either the BCA or AS1170.0 Table F, found in Admt 2-2003 and later revised in Admt 4-2005.
Now, the BCA has two values, for Importance Category (IC) 1,2 and 3 buildings an exceedence interval of 500 years is used and for IC4 buildings an exceedence interval of 800 years.
Conversly AS1170.0 further sub-divides the IC with design lifes and the exceedence intervals vary from 25 years for an IC1 building with a design life of 6 months, to 2500 years for a IC4 building with a design life of 50 years.
How have others been deriving there kp values when using AS1170.4-2007, are you using the exceedence intervals set-out in the BCA or AS1170.0 and why is there such a variation between the two documents.