Do we need to give continute to the alignment of flexural member (beam) in the region of Shear wall?
While analysing in ETABS, I found all beams safe except in the shear wall region of the building. What may be the solution?
 
Replies continue below

Recommended for you

It's quite possible that the beams near the shear walls are acting as tie-beams between lateral elements or collectors/drag struts. You need to take those effects into account in your design, or detail out the potential for that load transfer if possible.
 
Perhaps your beams are moment connected to your shear walls and, as a result, acting like outrigger beams in a way that was not your intent?
 
You have to figure out WHY the beams are failing. What type of loading (axial, shear, strong axis bending, weak axis bending) is causing them to fail? And, where it that loading coming from?
 