At our federal agency we have at our Main Substation two 69/12.470kV, 15/20MVA, transformers feeding two walkin breaker lineups. Each lineup is fed from one transformer and the two lineups are connected by a NO tie ACB. Presently the transformers are protected by S&C Fuses. Soon S&C Trans-rupters will be installed to provided primary switching. The S&C Trans-rupters were purchased with Basler OC relay system.
Belately, it was decided to also provide transformer differential protection. A Basler system will used.
Can the Basler OC system be used as a backup to the Basler 87T?
Management may decide to forego the 87T system and stick with the 50/51 system. Will it offer sufficient protection for transformers in this size range, considering that the replacement value per transformer is not insignificant.
Thank you!