Received a geotechnical report for a project site that has expansive clay soils. In the report is states that the belled pier capacity is to be reduced when the spacing of the bells is less than 3 bell diameters (clear space) based on the larger pier. The reductions are 40% for 2-3 diameters and 60% for 1-2 diameters.

Given that some of our columns are spaced rather closely together in certain areas we can't get many of the piers to converge on a solution. Does anyone have any literature on reduced capacity of belled piers based on proximity to other piers. I need some background knowledge so that I can convince the geotech to ease up on these reductions.



 
Replies continue below

Recommended for you

In the general, there is a reduced permitted loading because of zone of influence overlaps. It is not just for belled caissons. Check out Tomlinson or other foundation texts that discuss the topic.
 
Perhaps spread out the piers and use a pier cap between them to support the structure offset from the piers?

Check out Eng-Tips Forum's Policies here:
faq731-376
 
TXEng88 - Their may be an answer for you. You mention that the geotech's report states:

"...that the belled pier capacity is to be reduced when the spacing of the bells is less than 3 bell diameters (clear space)."

Spacing of 3 diameters is the commonly accepted spacing to prevent group action. This applies to both driven piling & drilled piers, whether they are point bearing or friction.

The loop hole you can present is that all credible references that I'm aware of measure the 3 diameters from center to center, not clear space - that is a big difference. Check out references such as "Principles of Foundation Engineering", by Braja Das. Also, make sure that you are reading the report correctly.

[idea]
[r2d2]
 
I'd get back to the geotech and ask if a lowered elevation of support might be considered to use at the currently recommended bearing pressure. I suspect the support capabilities there would be higher, meaning overlap concerns would be reduced.
 
Usually the limit we see is a spacing of 0.5 the bell diameter between bells. We deal with this a lot when we get into bin structures. These guidelines are usually quite arbitrary and if one is willing to pay the geotech to investigate a specific case it can save quite a bit of headache.

The pile diameter rule usually applies to skin friction piles, so it might be worth a call. The bell interaction should have more to do with the bulb around the bearing region. We put a lot of piles in CH or CM clay.
 