tikitime
Mechanical
- Apr 9, 2002
- 23
I have an industrial building in which the ahu's are being replaced. The units are 10,000 - 15,oo cfm units. The new units will be set to provide 100% OA during the occupied hours due to chemicals in the building, and minimum OA during the unoccupied hours. The new units will have VFD's. The building owner is concerned about reducing the amount of reheat. Also, due to funding, the only energy savings device on the new units will be the vfd's - as compared to using a heat wheel or the like. The ahu's will use chilled water and hot water.
The ahu vendor and building owner disagree on the the ahu configuration that will work the best. The vendor is suggesting a typical draw-thru unit with a single cooling coil and heating coil. He wants to use the control valves to control the load and use reheat when required.
The building user has suggested using a mixed air bypass unit or a unit with two cooling coils stacked on top of each other - a smaller one on top for the RA and a larger one on the bottom for the OA - the airstreams mix prior to the coil.
Any input on which is the better way to go?
The ahu vendor and building owner disagree on the the ahu configuration that will work the best. The vendor is suggesting a typical draw-thru unit with a single cooling coil and heating coil. He wants to use the control valves to control the load and use reheat when required.
The building user has suggested using a mixed air bypass unit or a unit with two cooling coils stacked on top of each other - a smaller one on top for the RA and a larger one on the bottom for the OA - the airstreams mix prior to the coil.
Any input on which is the better way to go?