AdverseAdventure
We have sized our heat exchanger to meet the full demand of our process equipment, but for 75% of the time we will need to run at 1/3 capacity. We have a closed loop 45F chill water supply and a closed process water loop that operates three machines with a 250gal open atmosphere tank. Each machine outputs 200,000 BTU/h at full load. So, basically, we will have a 100,000 - 600,000 BTU/h variable load.
Our vendor for the heat exchanger knows nothing about controls equipment, they can only punch numbers in their calculator and spit out a resultant size. Their numbers are OK as they match our approximations for # of plates and surface area.
The real question:
Can I throttle the cooling capacity of the heat exchanger by using a PID controlled globe valve that reacts based on my process water temperature? Is it a good idea to PID control the chill water as well? I would rather not have the heat exchanger condensing water out of the air when heat load from machines is minimal. I need to maintain a specific temperature range +-20F. Too cold and the machines will not warm up, too hot and they will overheat. What are the implications of this? I would install a bypass on the process side so that when the globe valve closes it will divert the water so the full flow is always dumping back into the 250g tank.
The real question: