Can the bladder tank and associated piping for a Hi-Ex foam system be in the same room as the Fire Pump and Controller?
According to NFPA 11 (2005) Section 4.2.2.1 states that pumps shall be installed IAW NFPA 20.
NFPA 20 (2007) Section 5.12.1.1.4 states: "Rooms containing fire pumps shall be free from storage and penetrations not essential to the operation of the pump and related components."
Since a bladder tank "stores" concentrate and neither the tank or the concentrate is essential to the operation of the fire pump, do I have to provide a separate room for the foam equipment?
Based on a strict reading of both standards it appears that I will need separate rooms. Do you agree?