dreidpc:
I have to guess that you're running a gas well or a tank battery sevicing gas or gas/oil wells with associated produced water and flash gas from heater-treater(s) & separators. The produced water is stored in API tanks pending disposal methods. In the process of storage, flash gas is deposited in the produced water tank as the pressurized separators dump their separated produced water into it; plus, the produced water emits dissolved gas as well.
In the "old days", we didn't care about the flash gas and much less about the dissolved, emitted gas. We just let them vent out into the "Big Dumpster" - the atmosphere. Things have changed and VRUs (Vapor Recovery Units) are now mandated to recover (instead of emitting) the gas vapors from the tank. [at the this point I want to mention that you really owe the United Way $15 instead of $5 - you also sinned on SAGD and VRU]
The way you describe your system, you seem to have the produced water tanks connected to the suction line to the VRU - which is OK, depending on your controls and instrumentation - and all the gas going to the VRU is originating in your upstream, flowline separators. I can't understand why your DBM calls for a purge on a time basis. The way I design this type of system - and I've done a bunch in the last 14 months - is that I send my separated vent gas to a Low Pressure Surge drum where I control the suction pressure to the VRU. I employ High Pressure gas source as my produced water tank blanket source. I use a regulator to adjust the pressure to the tanks and any venting required from the tanks is sent to the suction of the VRU - whenever that occurs or is needed. This way, I don't subject my produced water tanks to a possible very low pressure in the VRU suction line caused by excess capacity in the VRU compressor.
I suspect your system has a lot of heavies (C3+) and you may be forming a layer of light condensate floating on the top of your produced water. This will happen if you don't have a skimming operation. If that is the case, the intermittent purge may be a tool to try to avoid too much hydrocarbon lights condensing in the produced water tank. But I'm just guessing at this stage. Normally, I would not give importantance to the need for intermittent purging as you have described it. However, I would keep my eye on the amount of hydrocarbon condensate floating on top of your water layer. This can be a potential hazard condition if left unaccounted for.
There is no way that I, or anyone else, could give you even approximate purge rates. I'm sorry if I haven't been of much help, but without being there and seeing the entire process, it's very difficult to advise on something we are unfamiliar with. I can only give you examples of what I have and continue to do here in the Texas oil patch.