Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Blast Resistant tilt wall design and separtion distance ...

Status
Not open for further replies.

mw001

Specifier/Regulator
Jul 1, 2007
2
I am in need of the specific 'blast resistant' design criteria and codes for the construction of a Petro Lab Analysis building sited on a Petro Plant facility. I also need to determine the minimum separation distance the proposed building can be from the refinery area.
 
Replies continue below

Recommended for you

For the answer to the "Distance" part of your question see the Final report on the BP Refinery Explosion.

I think they have set a distance of 1980 feet from a hazard and occupied buildings.
 
The second URL in pennpiper's post references an API Recommended Practices # 753, "Management of Hazards Associated with Location of Plant Portable Buildings, 1st Edition, December 2006."

This publication should be available now.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor