Block Valve in the Relieving Path of Fixed CO2 Extinguishing System 1

Status
Not open for further replies.

ripaldee

Mechanical
Jun 16, 2011
22
0
0
SA
NFPA 12 requires the installation of pressure relief device in closed piping sections of the fixed CO2 extinguishing system. My question is: Does the standard requires a block valve in the relieving path of the pressure relief device?
 
Replies continue below

Recommended for you

I can't be sure, not having read NFPA, but I've not seen where any code reqires a block valve in front of a relief valve, no matter how much some people like to put them there.

If you do put one there, be sure you can seal-lock it open.

We will design everything from now on using only S.I. units ... except for the pipe diameter. Unk. British engineer
 