Hi,
since starting my carreer with a water treatment company, I’ve always calculated boiler blowdown using the following formula:
BD = evap rate / (cycles -1)
This is an equation that I learned in cooling tower training but I’ve always used it for boilers too by replacing evap rate with steamrate. However, after a customer looked at me funny when I calculated their boiler blowdown I found the formula below, which gives you a different answer:
(1/cycles) * steamload = BD
Can you help me understand why there is a difference between the way cooling tower blowdown and boiler blowdown are calculated? I can't wrap my mind around why there would be a difference in the way cycles are calculated for the two since they both have makeup, blowdown, cycles, and steam. What am I missing here?
thanks.
since starting my carreer with a water treatment company, I’ve always calculated boiler blowdown using the following formula:
BD = evap rate / (cycles -1)
This is an equation that I learned in cooling tower training but I’ve always used it for boilers too by replacing evap rate with steamrate. However, after a customer looked at me funny when I calculated their boiler blowdown I found the formula below, which gives you a different answer:
(1/cycles) * steamload = BD
Can you help me understand why there is a difference between the way cooling tower blowdown and boiler blowdown are calculated? I can't wrap my mind around why there would be a difference in the way cycles are calculated for the two since they both have makeup, blowdown, cycles, and steam. What am I missing here?