Hi,
ARGUMENT:
The argument is that a 500 watt PSC motor will create 1706 Btu's of heat thus increasing the return air temperature. Since RAT has a significant effect cooling capacity, the assumption is that you must include this heat given off by the blower motor into system load calculation. If true, then the blower motor heat is equal to 6,141,000 Btu/h.
QUESTION: What is the amount of temperature rise that the blower motor heat can give off?
We can assume a test condition of 1600 CFM's at 78 DBT, 63 WBT in a space of 2.7 cu. ft. (20" x20" blower cabinet) at sea level.
OPINION: Given the volume and flow rate, I do not think there is a detectable amount of heat gain to measure a delta T.
Let's try to put this question to bed. The result may change Manual J forever.
ARGUMENT:
The argument is that a 500 watt PSC motor will create 1706 Btu's of heat thus increasing the return air temperature. Since RAT has a significant effect cooling capacity, the assumption is that you must include this heat given off by the blower motor into system load calculation. If true, then the blower motor heat is equal to 6,141,000 Btu/h.
QUESTION: What is the amount of temperature rise that the blower motor heat can give off?
We can assume a test condition of 1600 CFM's at 78 DBT, 63 WBT in a space of 2.7 cu. ft. (20" x20" blower cabinet) at sea level.
OPINION: Given the volume and flow rate, I do not think there is a detectable amount of heat gain to measure a delta T.
Let's try to put this question to bed. The result may change Manual J forever.