We have a relatively new Aaon HVAC system (2 Years) with a 4 stage compressor control circuit. We have a problem where the contactor coil for the 4th stage fries about every 2 months. The control circuit for each compressor is fairly simple. The only interlocks in the circuit are the low and high pressure switches for the compressor and a 5 minute delay on timer. The circuit is powered by three 480 to 24VAC, 75VA transformers wired in parallel for a total of 225 VA. The unit was originally supplied with 2 xfrmrs, but somebody added a third one shortly after the unit was installed. My feeling is that the xfrmrs may be unbalanced which may be causing the coil to fail on the 4th stage. The first 3 stages pretty much are on all the time with the 4th stage cycling on/off as needed. All 4 stages are wired identically except that someone upgraded the contacts on the 4th stage contactor from 25amps to 40amps. Others remain at 25amps.
Some other info: we usually melt the TON relay also, since about 9.6 amps start flowing through it and the three xfrmrs have internal 3.2A circuit breakers that never trip when the coil melts.
Anyone have any other ideas as to what might be causing this.
Thanks
Dave
Some other info: we usually melt the TON relay also, since about 9.6 amps start flowing through it and the three xfrmrs have internal 3.2A circuit breakers that never trip when the coil melts.
Anyone have any other ideas as to what might be causing this.
Thanks
Dave