buddy91082
Electrical
- Jan 22, 2009
- 169
We are installing bms panels (these are local DDC panels) to control our air handling units. The vfds and/or starters controlling the AHUs are located remote from the BMS panels.
Fire alarm shut down of the units will be activation of the respective duct smoke detectors. We are installing fire alarm control modules within 3'-0" of the BMS panels. The fire alarm systems, upon activation of the duct smoke detectors, would tell the bms panel to shut down the ac units through the vfd/starters.
Question 1 - does the fire alarm control module need to be located at the vfd/starter or can we locate it at the bms panel (DDC panel?
Question 2 -performing the shutdown through the bms panel, does the bms panel require a UUKL or UL 864 listing?
References to code chapter & verse would be helpful.
thanks.
b
Fire alarm shut down of the units will be activation of the respective duct smoke detectors. We are installing fire alarm control modules within 3'-0" of the BMS panels. The fire alarm systems, upon activation of the duct smoke detectors, would tell the bms panel to shut down the ac units through the vfd/starters.