Boiler Hydro

Status
Not open for further replies.

Rpsfinest

Electrical
Dec 8, 2006
29
Looking for a standard procedure to do a boiler hydro on a small package boiler, safeties lift at 200 and 205 psi. Does anyone have a basic generic procedure or possibly a specfic one that I can modify?
 
Replies continue below

Recommended for you

What purpose do you intend the pressure test to serve?

Tests for new construction will have different criteria (and governing Code(s)) than post-construction, post-operation tests. Ditto for tests following repairs or alteration vs plain old pre-start-up leak tests.

For new...ASME Section I + local & State authorities.

For "old" w/repairs/alterations...NBIC + local & State authorities.

For leak tests...110% operating pressure or 85%-90% the relief valve set pressure(s).
 
RPS.....

In what state, county, contry or municipality are you located ?

Why are you doing the hydro ?

And most importantly, who is the governing body that will accept the test results ?


-MJC

 
Procedures for boiler hydrostatic testing, not test pressure requirements, are developed by boiler OEM's and repair organizations that hold a valid R- Certificate with the National Board. In other words, you need to write your own procedure and have it approved by your AIA of record.
 
Usually the boiler OEM provides a procedure writeup in the O+M manual.

Add'l precautions for a safe hydro can be found in the asme sect VIII, various paragraphs.
 