Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Boiler Stack Pressure Compensation

Status
Not open for further replies.

MNMaint

Mechanical
Jan 20, 2009
13
Hello,

I have three natural gas, commercial condensing boilers with forced draft burners. The stack terminates aproximately 30 feet above the boilers. They are experienceing too much draft and are cutting out on flame failure. Currently, there is no barometric damper in the breaching to the flue.

An engineer reccomended against a barometric damper and called, rather, for volume dampers in each of the boiler exhaust connections. In fact, he said the barometric damper would void the manufacturer's warranty.

I've never encountered this before. Any opinions / comments?

Thanks
 
Replies continue below

Recommended for you

What does the installation or operators manuals of those burners say?
 
Boiler manufacturers have the last say in barometric dampers. It depends on their UL approval. Using condensing boilers though, you are probably running a positive stack with AL29-4C venting (BH series).

In most cases barometric dampers are not allowed due to the positive draft however (cat IV), modifying the stack could increase the pressure in the stack to desirable levels.

A stack draft controller, although expensive is the best option for correct operation. It's ability to constantly adjust for pressure allows the burner to fire against it's correct design pressure therby prolonging it's life and reducing maintenance costs.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor