ajk1
Structural
- Apr 22, 2011
- 1,791
Need to design a couple of bollards to replace existing corroded away bollards that are at the roll-up doors of a police station. They are on an existing concrete slab. Is there anywhere that I can find a standard bollard design detail for this, or do I have to design it myself? There must be someone who has seen a well thought out typical detail.
I would think that would comprise a 42" high minimum (60" if visibility is a concern), minimum 6.5" O.D. minimum schedule 40 steel pipe, galvanized, filled with 35 MPa concrete, base plate of appropriate thickness welded with appropriate weld size, and 4 Hilti galvanized or s/s adhesive anchors of appropriate diameter. Painted yellow (after treating the galvanized surface appropriately so paint will adhere) for best visibility. Any detail that anyone can refer me too?
I would think that would comprise a 42" high minimum (60" if visibility is a concern), minimum 6.5" O.D. minimum schedule 40 steel pipe, galvanized, filled with 35 MPa concrete, base plate of appropriate thickness welded with appropriate weld size, and 4 Hilti galvanized or s/s adhesive anchors of appropriate diameter. Painted yellow (after treating the galvanized surface appropriately so paint will adhere) for best visibility. Any detail that anyone can refer me too?