For the first time I am stumped on a nut& bolt question in 20+yrs of experience!
We typically do not specify what type of nut, bolt and washer to use while termianting low volage cables (or anything for that matter). A good contractor normally uses grade 5 steel bolts with flat washers on both sides plus a locking washer on nut side.
A not so good contractor installed (on copper bus to copper lug connections)grade 2 steel bolts without any washers. Also some bolts were not protruding beyond the nut etc. We (Owner and I)want him to correct his work.
Besides being a good practice, I can not readily find any standard or code (In the USA) or even manufacturer's recommendations that requires proper way of installing nut and bolt connections specially for electrical terminations. Does any body know of such requirement in a 'enforceable' standard? NEMA, ASTM or such.
Funnily NEC has long write up as to how to install a screw terminal and wire nuts but no word on bolted connections
Specifying engineers please take note!
We typically do not specify what type of nut, bolt and washer to use while termianting low volage cables (or anything for that matter). A good contractor normally uses grade 5 steel bolts with flat washers on both sides plus a locking washer on nut side.
A not so good contractor installed (on copper bus to copper lug connections)grade 2 steel bolts without any washers. Also some bolts were not protruding beyond the nut etc. We (Owner and I)want him to correct his work.
Besides being a good practice, I can not readily find any standard or code (In the USA) or even manufacturer's recommendations that requires proper way of installing nut and bolt connections specially for electrical terminations. Does any body know of such requirement in a 'enforceable' standard? NEMA, ASTM or such.
Funnily NEC has long write up as to how to install a screw terminal and wire nuts but no word on bolted connections
Specifying engineers please take note!