I have a question regarding IEC60909 and bolted fault. Generally for a single phase to earth fault the current can be written as follows:
I''k1 = sqrt(3)*Un/(z1+z2+z0+3Zn+3Zf)
Where Zn is the impedance connected to neutral and Zf is the fault impedance. IEC omits the fault impedance and with solidy earthed system they write:
I''k1 = sqrt(3)*Un/(z1+z2+z0)
The consequence is that the current calculated will be more conservative compared to the current calculated with the fault impedance.
My question is therefore, why does IEC omit the fault impedance? Is it generally ok to omit this value?
Best Regards
Hussain