Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Bond Beam Location 2

Status
Not open for further replies.

twinnell

Structural
Jan 20, 2005
212
I have seen a note on drawings that requires bond beams to be placed above openings and where shown on plans and shall be placed no greater than 10'-0" OC vertically. Can anyone tell me where I can find anything that tells where bond beams should be placed, besides the top of the wall or when reinforcing is designed to span between bond beams. This note is a typical note and applies to all projects even though the reinforcing is designed for a span from foundation to roof.

 
Replies continue below

Recommended for you

One last remark from me...

You indicated that you have vertical reinforcing at 16" o.c. and are using truss-type joint reinforcing. I always specify ladder type joint reinforcing for walls with vertical reinforcing, as recommended in NCMA TEK 12-2B, as the diagonals can interfere with the rebar and grout placement.
 
JKW05 -

You are dead on about the ladder type being preferred for grouted walls. Also clipping cross wires is something I have never run across in 40 years. Any mason is smart enough to set the wire right and a rebar or wire can also be accomodated since at most it is 1/2" longitudinally.

Sometimes engineers always assume truss-type elements are better, which is not always true.

Dick
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor