Bonding of covers 1

Status
Not open for further replies.

richerdick32

Electrical
Joined
Feb 22, 2014
Messages
16
Location
GB
We have some large motors that have covers over the slip rings, the covers are removable using a standard panel key, should the covers have a bonding wire between the covers and the generator? I know electrical panel doors should be bonded?
If a bonding wire is required what size should it be? the main supply earth is 25mm2 are there any regulations I can look at for this?
 
The generic rule is that "Any conductive part that can get into contact with a lethal voltage during normal operation or any conceivable fault condition shall be permanently and securely connected to a reliable ground".

It is expressed in different ways in different standards. But that is the gist of it. The bonding braid/wire shall have enough capacity to carry the worst case fault current without melting (or getting too hot) until protection trips.

My pet is that a motor shaft needs to be grounded (permanently and securely) if both bearings are insulated or have ceramic balls.



Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
To richerdick32 (Electrical)(OP)

In the IEC world, the general opinion and practices are:

A. For motors
Motor slip rings removable covers, cable-box removable covers and the like; the usual [metal screwed connections or clamping force by the metallic locking mechanisms] are (considered sufficient to ensure earthing continuity) [provided that no electrical equipment is attached to them]. No PE-conductor is required to be attached on them.
Note: For conductive parts where no electrical equipment is attached to them; if preferred but not mandatory:
a) may be earthed by a flexible bare conductor or with (transparent) sleeving, or with an insulated colour-coded PE-conductor with colour-code, see detail C below.
b) the PE-conductor, bare or insulated shall be NOT smaller than 2.5sqmm of copper material. Larger size if aluminium conductor is used.

B. For electrical panels {See IEC 60439)
" For lids, cove plats and the like, the usual screwed connections and metal hingers are considered sufficient to ensure continuity provided that [no electrical equipment is attached to them]"
Note: For conductive parts where electrical equipment [exceeding the limits of extra-low voltage] are attached to them:
a) steps shall be taken to ensure continuity of the protective circuits.
b) the (copper) PE-conductor [shall not be smaller than 2.5sqmm] but [need not be larger than the largest wire size wired on the equipment] attached on them.

C. PE-conductor colour-code per IEC
a) PE-conductor may be
- bare (no painting of colour is required),
- bare with (transparent)sleeving,
- insulated with colour-coded "yellow/green"
Attention:1. Except "yellow/green" coloured-coded insulated conductor, NO other colour-coded conductors shall be used as PE-conductor.
2. "Yellow/green colour-coded insulated conductor shall NOT be used for phases or neutral conductor.
 