I am working on a small facility project in which we are installing a wet pipe sprinkler system. In order to meet pressure/flow demands of the system, we are providing a small (750 gpm/50 psi) pump to supplement the available city water supply. I have concluded that we do not need a jockey pump due to the available static pressure in the city water main (98 psi @ 530 gpm), which should be more than adequate to maintain pressure in the system piping. In addition, using the recommended sizing guidelines for a jockey pump provided in NFPA 20H, the recommended size of a jockey pump for this size fire pump is less than what is available from the city suppy (NFPA 20H recommends a jockey pump of 7.5 gpm @ 60 psi).

For these reasons, I have concluded that a Jockey Pump is not required; is there something that I am missing or any error in my logic?
 
Replies continue below

Recommended for you

Your facility's system will now depend upon the City maintaining sufficient water pressure to pressurize your system. Probably fairly safe, but why take a chance for such a small pump?
 
Agreed, in theory safe, however - your reasoning assumes that the towns pressure will always be above the designed minimum pressure.

It is a capital mistake to theorise before one has data. Insensibly one begins to twist facts to suit theories, instead of theories to suit facts. (Sherlock Holmes - A Scandal in Bohemia.)
 
I would leo go without the jockey pump. If the pressure drops below the design minimum it seems unlikely to me that there will be water at all to boost - at least for any significant time to make a difference (what I'm trying to say is that low pressure==disruption of service)
 
Denver:
#1. I suggest you have an informal conversation with the Local Fire Marshal about your plan and the reasoning behind it.

#2. Leave space for the Jockey Pump(JP)

#3. Install Valved connections, properly located, sized and type, for the JP suction, JP discharge and the Pressure Sensor Switch.

prognosis: Lead or Lag
 