bmw318be
Mechanical
- Jun 16, 2010
- 197
Hi Sir,
Here's the situation: We retrofit a fuel system, We use centrifugal pumps that are sitting directly at the storage tanks to pump to existing day tank which is all at level 1, pressure is less than 2 bar maximum.
Now, our end user is build a new building with the day tank on the top level 4, 50 m vertical height. Pressure losses around 6 bar.
Assuming, distance between New Pump room of PD pumps is too far away, we would need to tie in to the existing centrifugal pump in order for the PD to have sufficient NPSHa as distance is a concern and it is not economical to build a new line.
Centrifugal flow is 600 LPM at shut off head of 50 m
Centrifugal discharge line is having a calculated frictional loss up to PD pump inlet is 22 m
PD pump rated flow is 200 LPM at 5 bar
Question 1:
If the centrifugal feed the PD pump which has a lower flow of 200 LPM, would the system pressure of centrifugal follow to 200 LPM since the maximum displacement of the PD is only 200 LPM ?
Question 2:
Assuming the centrifugal is able to operate at 200 LPM curve, can I say that the centrifugal pump able to feed well to the PD pump ?
Question 3:
Would the Inlet pressure before the PD pump inlet is 22 m, which is the frictional loss or it is close to 0 barg since PD pump would withdraw 200 LPM from 400 LPM at no pressure:
Question 4:
i see some discussion, for series, we need to have a balance flow, would the centrifugal on the inlet considered balance as it would adapt to the flow the PD pump displacing
Question 5:
Can I considered the inlet pressure as 0 barg so the NPSHa shall be around 10 m absolute. Assuming the inlet is packed
Question 6:
Is it recommend to install low pressure switch at 1 bar on the inlet of the PD pump so it would protect the PD pump in case no flow.
Here's the situation: We retrofit a fuel system, We use centrifugal pumps that are sitting directly at the storage tanks to pump to existing day tank which is all at level 1, pressure is less than 2 bar maximum.
Now, our end user is build a new building with the day tank on the top level 4, 50 m vertical height. Pressure losses around 6 bar.
Assuming, distance between New Pump room of PD pumps is too far away, we would need to tie in to the existing centrifugal pump in order for the PD to have sufficient NPSHa as distance is a concern and it is not economical to build a new line.
Centrifugal flow is 600 LPM at shut off head of 50 m
Centrifugal discharge line is having a calculated frictional loss up to PD pump inlet is 22 m
PD pump rated flow is 200 LPM at 5 bar
Question 1:
If the centrifugal feed the PD pump which has a lower flow of 200 LPM, would the system pressure of centrifugal follow to 200 LPM since the maximum displacement of the PD is only 200 LPM ?
Question 2:
Assuming the centrifugal is able to operate at 200 LPM curve, can I say that the centrifugal pump able to feed well to the PD pump ?
Question 3:
Would the Inlet pressure before the PD pump inlet is 22 m, which is the frictional loss or it is close to 0 barg since PD pump would withdraw 200 LPM from 400 LPM at no pressure:
Question 4:
i see some discussion, for series, we need to have a balance flow, would the centrifugal on the inlet considered balance as it would adapt to the flow the PD pump displacing
Question 5:
Can I considered the inlet pressure as 0 barg so the NPSHa shall be around 10 m absolute. Assuming the inlet is packed
Question 6:
Is it recommend to install low pressure switch at 1 bar on the inlet of the PD pump so it would protect the PD pump in case no flow.