I need some theoretical help on sizing a booster pump as I do not have all the information needed (at least not yet) to do it correctly.
I have an 800 ton chilled water system serving multiple air handling units. At some point in time, three new AHUs we added to the system and are served by a new 4" line that takes off from the supply and return mains. The 3 new units are served from the 800 ton plant during the winter, but not during the summer. The 4" pipes were cross-connected to another chilled water system after it was discovered that they could not get enough flow to these 3 new units during the summer. The 800 ton system is constant flow with 3-way valves; so, I'm sure they never had design flow but didn't need it during the winter.
They want to eliminate the other chilled water system and want to serve these 3 coils from the 800 ton plant. My problem is that I do not know the extent of the flow problem.
I have calculated that I need 328GPM @ 57' head to circulate water through the branch piping and 3 new coils. I'm not sure how to take it from here:
The 1st scenario would be that my central plant pump has enough flow capability, but just needs more head to reach these coils. But how much more? I don't have a flow or delta-P across the branch. If I size my booster pump for the full 55' head, that should be enough but probably overkill, right? I would use a triple-duty valve on the pump or balancing valve on the return line to just give me the 328GPM I need. Just a side note, which is better and why - Triple duty on the pump or circuit setter on the return line?
The second possibility is that the central pump is not large enough to give me the total GPM requirement. In that case, my booster pump head probably needs to account for its flow all the way back through the central pump, chiller, etc, correct? And will that cause issues since I will now be bringing more flow through the chillers?
I'm trying to obtain information on the central pump or better yet a balancing report of the system, but I don't know if they are available. I have been asked to select a booster pump to "fix the flow problem."
Are my lines of thinking correct? Any other ideas?
I have an 800 ton chilled water system serving multiple air handling units. At some point in time, three new AHUs we added to the system and are served by a new 4" line that takes off from the supply and return mains. The 3 new units are served from the 800 ton plant during the winter, but not during the summer. The 4" pipes were cross-connected to another chilled water system after it was discovered that they could not get enough flow to these 3 new units during the summer. The 800 ton system is constant flow with 3-way valves; so, I'm sure they never had design flow but didn't need it during the winter.
They want to eliminate the other chilled water system and want to serve these 3 coils from the 800 ton plant. My problem is that I do not know the extent of the flow problem.
I have calculated that I need 328GPM @ 57' head to circulate water through the branch piping and 3 new coils. I'm not sure how to take it from here:
The 1st scenario would be that my central plant pump has enough flow capability, but just needs more head to reach these coils. But how much more? I don't have a flow or delta-P across the branch. If I size my booster pump for the full 55' head, that should be enough but probably overkill, right? I would use a triple-duty valve on the pump or balancing valve on the return line to just give me the 328GPM I need. Just a side note, which is better and why - Triple duty on the pump or circuit setter on the return line?
The second possibility is that the central pump is not large enough to give me the total GPM requirement. In that case, my booster pump head probably needs to account for its flow all the way back through the central pump, chiller, etc, correct? And will that cause issues since I will now be bringing more flow through the chillers?
I'm trying to obtain information on the central pump or better yet a balancing report of the system, but I don't know if they are available. I have been asked to select a booster pump to "fix the flow problem."
Are my lines of thinking correct? Any other ideas?