Hi Guys:
I hope this is the correct forum for this question, here goes...
I have 'inherited' a design from a colleague for a fuel system
consisting of four 250 gallon fuel oil tanks feeding one 250 kVA emergency
diesel generator in a commercial office building.
I responded to a complaint that the machine prematurely ran out
of fuel, and discovered that the four tanks are piped in parallel, with
no bottom connected balance pipe. The top-connected oil pick-up pipes from all tanks are manifolded together into a common feed to the generator. The return from the fuel pump is arranged similarly. Unfortunately, the installer provided tanks with the incorrect number of connections and was forced to connect the fuel pump returns to the common vent pipe. I have reviewed all codes, and have found that other than the incorrect connection of the return to the vent pipe, there are no code violations.
Apparently, the generator runs out of fuel because the tanks all establish different fuel levels because the return does not refill all tanks evenly.
Personally, I see two options:
1) Add a day tank with fuel transfer pump from the larger combined tank. The day dank would have level switches to run the transfer pump, and the generator supply and return would be to and from the new day tank. I would also need to add an oil cooler to the day tank, secondary containment, and a oil detection sensor in the containment.
2) Scrap the tanks altogether, put in new ones with a bottom-connected balance pipe of appropriate size, and re-pipe the whole thing with the supply from the first tank, and the return to the last tank.
In your collective professional opinion, am I missing a simpler option? And could the existing tank arrangement (without bottom-connected communicating pipe) ever be made to work?
Best regards,
Daver
Ontario, Canada
I hope this is the correct forum for this question, here goes...
I have 'inherited' a design from a colleague for a fuel system
consisting of four 250 gallon fuel oil tanks feeding one 250 kVA emergency
diesel generator in a commercial office building.
I responded to a complaint that the machine prematurely ran out
of fuel, and discovered that the four tanks are piped in parallel, with
no bottom connected balance pipe. The top-connected oil pick-up pipes from all tanks are manifolded together into a common feed to the generator. The return from the fuel pump is arranged similarly. Unfortunately, the installer provided tanks with the incorrect number of connections and was forced to connect the fuel pump returns to the common vent pipe. I have reviewed all codes, and have found that other than the incorrect connection of the return to the vent pipe, there are no code violations.
Apparently, the generator runs out of fuel because the tanks all establish different fuel levels because the return does not refill all tanks evenly.
Personally, I see two options:
1) Add a day tank with fuel transfer pump from the larger combined tank. The day dank would have level switches to run the transfer pump, and the generator supply and return would be to and from the new day tank. I would also need to add an oil cooler to the day tank, secondary containment, and a oil detection sensor in the containment.
2) Scrap the tanks altogether, put in new ones with a bottom-connected balance pipe of appropriate size, and re-pipe the whole thing with the supply from the first tank, and the return to the last tank.
In your collective professional opinion, am I missing a simpler option? And could the existing tank arrangement (without bottom-connected communicating pipe) ever be made to work?
Best regards,
Daver
Ontario, Canada