"The first step in any grounding design is to obtain accurate soil resistivity data. Second, it is necessary to determine which grounding configuration will give a specific resistance within the installation area. This can be determined by using formulas (IEEE Standard 142, Green Book) or nomographs for calculating the resistance of a single vertical rod. If the target earth-ground resistance is not achieved, it is necessary to use multiple rods, or another arrangement."
Another recommendation is that you contact a firm specializing in grounding system design. Grounding is a scientific process and one on which equipment protection and human safety are critically reliant. Define exactly what grounding installations and improvements will work best for your site. This eliminates trial and error, and reduces the overall cost of the grounding system by designing only what is needed to meet your specifications.
The most common is Single Vertical Rod Design. I have installed many of these systems using a grid approach, attaching the equipment to the grid with CLAD welds.
The earth-ground resistance for a single electrode, such as a driven rod or electrolytic rod, can be calculated from the following formula:
R = r/2 p(l(2l/r)(1 + 2K))
Where
R = Resistance (ohms)
r = Mean soil resistivity (ohm-cm)
l = Length of rod (cm)
r = Radius of rod (cm)
K = Coefficient