I am working on the connection design for a special concentric brace frame. I am a little confused as to what forces i am supposed to use for the design of the welds and gusset plate.
The 2001 CBC Section 2211.4 specifies the lesser of:
1. Design Tensile strength of brace (I assume this means per AISC Specs, fPn = 0.9FyAg)
2. Force from load combinations 3-7 and 3-8 (0.9D+Em and 1.2D+fL+Em)
Then for gusset plates, it rspecifies the compressive design strength of the brace (similarly, fPc = 0.85FcrAg).
Is this correct? This is different from the AISC Seimic Provisions, which specifies nominal tensile strength instead of design tensile strength (P=RyFyAg), which is where i got confused...
The 2001 CBC Section 2211.4 specifies the lesser of:
1. Design Tensile strength of brace (I assume this means per AISC Specs, fPn = 0.9FyAg)
2. Force from load combinations 3-7 and 3-8 (0.9D+Em and 1.2D+fL+Em)
Then for gusset plates, it rspecifies the compressive design strength of the brace (similarly, fPc = 0.85FcrAg).
Is this correct? This is different from the AISC Seimic Provisions, which specifies nominal tensile strength instead of design tensile strength (P=RyFyAg), which is where i got confused...