mb3928
Electrical
- May 27, 2020
- 26
This problem came up in the context of adding solar to a large warehouse built in the 1970s. Construction consists of steel W shape columns with cap plates, W21x68 Gerber (cantilever) girders with a column-to-column span of 50' and a cantilever of 7'. There are no web stiffeners at the column connections which I know is probably deficient. Atop the W21x68s are W12x14s which are also constructed as cantilever joists and spaced at 8'4" OC with a girder-girder span of 25' and a cantilever of 4'. The deck is 8'4" x 2' x ~3" precast concrete C channels which are clipped to the W12x14s. The manufacturer's literature for the precast planks provides an allowable load of ~120 psf.
The structural engineer (I am the contractor) is saying that the W21x68s need bottom chord bracing at every location they cross a W12x14, and that the W12x14s need continuous bottom chord bracing in (2) locations per span.
I am by no means an expert, but this seems excessive to me and I am seeing that most current specifications e.g. AISC 360-16 only call for bracing at column locations. Is the specified bracing reasonable?
The structural engineer (I am the contractor) is saying that the W21x68s need bottom chord bracing at every location they cross a W12x14, and that the W12x14s need continuous bottom chord bracing in (2) locations per span.
I am by no means an expert, but this seems excessive to me and I am seeing that most current specifications e.g. AISC 360-16 only call for bracing at column locations. Is the specified bracing reasonable?