This problem came up in the context of adding solar to a large warehouse built in the 1970s. Construction consists of steel W shape columns with cap plates, W21x68 Gerber (cantilever) girders with a column-to-column span of 50' and a cantilever of 7'. There are no web stiffeners at the column connections which I know is probably deficient. Atop the W21x68s are W12x14s which are also constructed as cantilever joists and spaced at 8'4" OC with a girder-girder span of 25' and a cantilever of 4'. The deck is 8'4" x 2' x ~3" precast concrete C channels which are clipped to the W12x14s. The manufacturer's literature for the precast planks provides an allowable load of ~120 psf.
The structural engineer (I am the contractor) is saying that the W21x68s need bottom chord bracing at every location they cross a W12x14, and that the W12x14s need continuous bottom chord bracing in (2) locations per span.
I am by no means an expert, but this seems excessive to me and I am seeing that most current specifications e.g. AISC 360-16 only call for bracing at column locations. Is the specified bracing reasonable?