Barry1961
Industrial
- Oct 3, 2003
- 530
We have a customer that makes small carnival rides that wants to slow down and stop them as quickly as possible. This rides is a horizontal disc that spins with "cockpits" on a 16' diameter that people ride in.
The specs now are roughly....
3000lb on a 16' diameter circle, 6330ft-lb kinetic
9 rpm top speed
120:1, 1hp reducer, 85% efficient, 3494in-lb
1.43:1 secondary reduction, chain & sprocket
Fincor 1hp, 5740 VFD, 115 1ph In, 230 3ph Out
N0 brake resistor option allowed
Supply voltage is 115VAC, 1ph
VFD is at 53hz
20 sec.ramp to stop
I am getting information on expected duty cycle.
He is trying to stop in 20 sec. and is getting an over voltage fault. I did some rough calculations and came up with a 28 sec. ramp being about the quickest I would expect possible with SF and efficiency helping.
So far I have suggested going to a 160:1 reducer and run VFD at 69hz. This would give him roughly 33% more braking torque which would almost get him to the 20 sec. The reduced torque at 69hz should not be a problem with this mainly inertia load.
I was told by Fincor a brake resistor would not help with a 1hp motor at 230VAC so it was not offered.
Are there any tricks or alternate ways to brake quicker with a VFD without causing a fault?
What percent of full load motor torque should I be able to decell at? 115%?
Barry1961
The specs now are roughly....
3000lb on a 16' diameter circle, 6330ft-lb kinetic
9 rpm top speed
120:1, 1hp reducer, 85% efficient, 3494in-lb
1.43:1 secondary reduction, chain & sprocket
Fincor 1hp, 5740 VFD, 115 1ph In, 230 3ph Out
N0 brake resistor option allowed
Supply voltage is 115VAC, 1ph
VFD is at 53hz
20 sec.ramp to stop
I am getting information on expected duty cycle.
He is trying to stop in 20 sec. and is getting an over voltage fault. I did some rough calculations and came up with a 28 sec. ramp being about the quickest I would expect possible with SF and efficiency helping.
So far I have suggested going to a 160:1 reducer and run VFD at 69hz. This would give him roughly 33% more braking torque which would almost get him to the 20 sec. The reduced torque at 69hz should not be a problem with this mainly inertia load.
I was told by Fincor a brake resistor would not help with a 1hp motor at 230VAC so it was not offered.
Are there any tricks or alternate ways to brake quicker with a VFD without causing a fault?
What percent of full load motor torque should I be able to decell at? 115%?