ryguy1116
Electrical
- Feb 24, 2005
- 3
I have a question in regards to neutral distribution.
I have a 400VAC(pri)/230VAC(sec) 5kva transformer.
The "hot" line goes to a distribution block and then is distributed to 4 branch circuits each branch circuit is protected with a 10A circuit breaker.
The neutral is grounded then goes to a distribution block.
Is it ok to isolate each branch circuit with its own neutral?
The intent is not to overload the neutral and be forced into running a larger gauge wire. Each branch neutral line would be identified with a specific branch tag and specific wire #.
Example:
The first branch circuit "CB1" would be identified as "Control #1 (#1)". It's neutral would be identified as "Control Neutral #1 (#1A)"
The second branch circuit "CB2" would be identified as "Control #2 (#2)". Its neutral would be identified as "Control Neutral #2 (#2A)".
Is this addressed in NEC?
I have a 400VAC(pri)/230VAC(sec) 5kva transformer.
The "hot" line goes to a distribution block and then is distributed to 4 branch circuits each branch circuit is protected with a 10A circuit breaker.
The neutral is grounded then goes to a distribution block.
Is it ok to isolate each branch circuit with its own neutral?
The intent is not to overload the neutral and be forced into running a larger gauge wire. Each branch neutral line would be identified with a specific branch tag and specific wire #.
Example:
The first branch circuit "CB1" would be identified as "Control #1 (#1)". It's neutral would be identified as "Control Neutral #1 (#1A)"
The second branch circuit "CB2" would be identified as "Control #2 (#2)". Its neutral would be identified as "Control Neutral #2 (#2A)".
Is this addressed in NEC?