Brazing Copper Earth Tape

Status
Not open for further replies.

peterpylon

Electrical
Oct 23, 2001
12
The spec is that all copper earth tape joints must be brazed. Fault level is 15kA. Size of tape is 50mm x 6mm (300mm²)
What should the joint overlap measure and what is the best filler material to use to gain optimum strength and conductivity? Would a butted "T" joint be acceptable IE contact surface 300mm².
Comments very much appreciated.
 
Replies continue below

Recommended for you

Thanks Alehman, Yes I've used this kind of joint on buried tape joints. They are very good. But if you've got a client etc who wants the joints brazed, well you have to do it. I need to know what is used as the most cost effective method.
Type of gas torch.
Type of flux.
Type of filler.
temperature etc.
Types of joint etc. etc.
 