Dear Folks,
Pl. advice me for breaker and Switchgear ratings.
We have 9-AC generators are connected in parallel without grid supply. All neutrals are solidly grounded without neutral breaking during parallel operation. Fault levels are calculated by ETAP software and these values are as follows.
ANSI calculations (Device duty- 3ph):
Fault currents on Main Bus:
Interrupting Duty: 156.506kA symmetrical rms
Momentary Duty:245kA Assymmetrical kA rms & 410.080kA Assymetrical kA crest.
Steady state current:56kA rms (calculated manually)
Based on the above values, pl. advice for switchgear outgoing breakers MAKING AND BREAKING CAPACITY, SHORT CIRCUIT WITH-STAND CURRENT for 1-sec and Switchgear BRACING CURRENT & SHORT-CIRCUIT WITHSTAND CURRENT for 1-sec.
Advanced thanks for your replies and discussion.