Thanks for the responses so far. I am just getting into the details of the project right now.
This is to be a "smart grid" substation, with the intention of doing away with traditional lock out relays, trip/close switches, etc. Everything is to be operated via HMI through SEL protection logic processors or Novatech Orion Communications processor. That part I get.
The substation is 161kV, 4 lines, 2 transformers and 9 SF6 breakers. The line relaying is SEL 421 (Primary)& 311C(Secondary), with PLC based POTT scheme, 2 shot reclosing with HBDL supervision. There are two sets of station batteries for secondary relaying, 2 trip coils on the breakers. The SEL relays are equipped with the high-speed/ high-interrupting contacts. This is where things get convoluted.
The SEL relays are not utilizing the optional high-speed / high-interrupting contacts, but rather the standard rating contacts and one trip signal is sent from SEL to ABB combiflex Aux Tripping relay. From what I've researched about the ABB relays, they have an ~4ms operate time and are rated no higher in interrupting capacity that what the SEL relays have. In addition, there are literally 4 FT test switches from SEL to ABB to breaker trip coil. The scheme is similar for the secondary protection. I could understand the need for an Aux relay if there were concern about the SEL relay contact ratings or the need for contact multiplication. I've never heard of any problems with the high-speed/ high-interrupting ones. I fail to see why the relay, which has probably 10 unused contacts would not be utilized and why would anyone want to add so much additional wiring, devices and a quarter cycle delay?
I haven't fully investigated the 87B scheme, however it does incorporate SEL 487 and GE B90 relays. I see the ABB combiflex relays here, but would expect them to be acting as a LOR.
I have duly noted the discussions on the 87B as listed above.
Thanks