Mbrooke - I must have been sleepy too. I just re-read what I posted and there are a few mistakes there. But in general I think we're talking about the same thing. The 'advanced' pallet was something I saw all the time when I got into the business 10 years ago working mostly at older sites. I don't see 'advanced' pallets come with new fast SF6 breakers, but we still designate one as 'advanced' and try our best to set it accordingly. '62' is just to denote a timer. Our breaker fail has 3 paths (another lie but I'll explain later). Our 62a path is meant to pick up mechanical failure of the breaker, which is why the 'advanced' pallet is used. So if the mechanical operation of your breaker is slowing down or if the linkage falls to pieces, in theory the 62a will time out before the expected change in mechanical position and trip the zone. I like to set my 62a by adding two cycles to the actual measured contact opening time done during commissioning, with 75ms being the max. 62b picks up electrical failures. So the breaker 'opened' but there's still current. For this we use a 52/a pallet and an overcurrent element. If the breaker looks open but there's still current -> trip the zone. This timer I've seen set between 90 - 180ms. 62c path is what I really screwed up above. It's not just a time backup, nor is it for 400ms

62c is a last ditch effort in case the 62a and b timers don't go but another protection is continuing to call for a trip. We consider this to be an uncleared low magnitude fault scenario. It's supervised only by 52/a and a timer. For LV breakers we use 300ms and 500ms on high voltage breakers, to coordinate with adjacent zone 2 timed back up protections (400ms).
The fourth path I eluded to above is the early trip path. It's my favorite path. It's a protection against the workers

So when a worker is doing breaker fail maintenance and accidentally picks up a breaker fail trip bus (very very bad thing to happen during routine maintenance, but also very very easy to do) the early trip path will just trip the breaker you're working on, which, unless the breaker actually decides to fail at that moment, should defeat all the 62 path timers and cancel the breaker fail zone trip. Breaker fail protections generally don't trip the breaker they are a part of, rather the breakers of the surrounding zone. A miss-operation causing breaker fail to fire is a bad place to be.
Newer IED's will often have their own internal 'breaker fail' logic. This is going to be different depending on the manufacturer. We're ok using some of them, but others we might not. It's always an option to deploy the philosophies described above in the logic. Some of the manufacturers have their own internal breaker fail elements that are basically what I described above.