Breaker ratings?

Status
Not open for further replies.

gadero

Electrical
May 30, 2003
23
I've seen more than one client's standard requiring 22kAIC breakers on all 208Y/120V systems. 10k breakers are unacceptable. When asked why - I've always heard "That's the way we've always done it," or "It's our standard." Is there a good reason (or any reason) for this requirement?

Thanks
 
Replies continue below

Recommended for you

One reason might be to allow future increases in transformer size without replacing the breakers. You might get by with 10 kA breakers with a 5% impedance 150 kVA transformer. If the load increased in the future to require a 300 kVA transformer, you would be in trouble.
 
Plan carefully though. 22kAIC breakers are expensive compared to 10k.
 