I have a technical question. I'm hoping you can help me out.
At the local convention center they have seventy-five 300 kva GE K Factor transformers for temporary show power.
Each transformer is protected by a GE 500 amp SGLA36AT0600 current limiting circuit breaker.
These transformers have no loads for days at a time and the convention center would like to turn the transformers off during downtime.
(They are unloaded during switching and installed in an air conditioned tunnel).
This could save about $500 a day on the power bill.
I have reports of the breakers sometimes tripping when the transformers are re-energized. (I assume this is inrush current at a bad time in the cycle.)
I can find no problems with the transformers.
My Question:
Will re-energizing the tripped breaker two or three times in a row damage the breaker or damage the transformer?
Is it ok to use this breaker to turn this unloaded transformer on/off a few times a week?
Thanks,
Andy
At the local convention center they have seventy-five 300 kva GE K Factor transformers for temporary show power.
Each transformer is protected by a GE 500 amp SGLA36AT0600 current limiting circuit breaker.
These transformers have no loads for days at a time and the convention center would like to turn the transformers off during downtime.
(They are unloaded during switching and installed in an air conditioned tunnel).
This could save about $500 a day on the power bill.
I have reports of the breakers sometimes tripping when the transformers are re-energized. (I assume this is inrush current at a bad time in the cycle.)
I can find no problems with the transformers.
My Question:
Will re-energizing the tripped breaker two or three times in a row damage the breaker or damage the transformer?
Is it ok to use this breaker to turn this unloaded transformer on/off a few times a week?
Thanks,
Andy