I am on an offshore oil production platform. We have a 440V Diesel gen set running in island mode, supplying an emergency sw board. We attempted to auto sync our normal 440v power board fed from GT alternators through an intertie breaker
Normally the intertie ACB breaker closes at sync and the Emergency generator incomer ACB breaker opens normally after 2 secs. However, the intertie ACB closed and after a short delay (~2 sec) the Emergency generator ACB tripped on G Protection with fault current Ig = 675A. The intertie breaker stayed close, so we did not lose power to the em board
This is since we replaced the incomer ACB with a new modern breaker supposed to be like for like and all protection settings the same
There is no genuine earth fault as gen was running fine for a couple of days on own
The emergency incomer breaker is an ABB 3P emax 2 with neutral sensor replacing an obsolete emax breaker with neutral sensors
we are all baffled why the trip occurred, we don't believe there was a sync issue
any thoughts?
Normally the intertie ACB breaker closes at sync and the Emergency generator incomer ACB breaker opens normally after 2 secs. However, the intertie ACB closed and after a short delay (~2 sec) the Emergency generator ACB tripped on G Protection with fault current Ig = 675A. The intertie breaker stayed close, so we did not lose power to the em board
This is since we replaced the incomer ACB with a new modern breaker supposed to be like for like and all protection settings the same
There is no genuine earth fault as gen was running fine for a couple of days on own
The emergency incomer breaker is an ABB 3P emax 2 with neutral sensor replacing an obsolete emax breaker with neutral sensors
we are all baffled why the trip occurred, we don't believe there was a sync issue
any thoughts?