We have planned to install a LED fixture Model: VMV7L with an inrush current of 49.2 A. The duration of the inrush current is between 368 µs – 624 µs.
I'm yet to decide on number of LED fixtures to be connected in one circuit.
Say, if I connect 10 fixtures in one circuit, approximately 500A of inrush would be there when the breaker is turned ON.
The TCC curve of the EATON breaker is attached. Does the shaded portion in the TCC curve mean the "Minimum Interrupting time" of the breaker at the instantaneous portion?
My concern is the nuisance tripping of breaker for the Inrush current.
Will the breaker not trip because of sensing such a high inrush current value because the duration is way below the 0.001 sec.?
Kindly give your thoughts.
I'm yet to decide on number of LED fixtures to be connected in one circuit.
Say, if I connect 10 fixtures in one circuit, approximately 500A of inrush would be there when the breaker is turned ON.
The TCC curve of the EATON breaker is attached. Does the shaded portion in the TCC curve mean the "Minimum Interrupting time" of the breaker at the instantaneous portion?
My concern is the nuisance tripping of breaker for the Inrush current.
Will the breaker not trip because of sensing such a high inrush current value because the duration is way below the 0.001 sec.?
Kindly give your thoughts.