As I understand it the breaking capacity of an IEC breaker is given by the "rated short circuit breaking" current in kVrms. My queries :
- Must the DC component be considered when determining whether an installed breaker rating is being exceeded, or is the rating a symmetrical rating?
- At what time during a fault must the fault current be considered? Can the IDMT curve of a relay be considered, or should the 'minimum contact parting time + a nominal time for relay operation' be used irrelevant of protection details? What is a reasonable time?
- When using the IEC60909 method with max. C factor the fault current is higher than the ANSI C37 method. Say the IEC current exceeds the breaker rating and the ANSI doesn't what does one do. Any opinions or comments welcome.
- Any comments on the subject would be appreciated.