MohawkNE
Structural
- Apr 4, 2013
- 6
I am jacking a bridge to replace some bearings. I'm erecting temporary columns on each side of the pier column and placing jacks at the tops to lift the structure under full dead and live load.
At the bottom of the columns I am bearing on the old pier footing. My temporary columns are made up of four ibeams with bearing plates. AASHTO bearing pressure loads are just within limits, but I am analysing the footing for the excentric loads of the temp jacking columns.
The existing footing is on piles with the pier pedestal in the center and is six feet thick. It looks like it's designed correctly. My temporary jacking structures are located outboard of the pier column and extend to the edge of the footing. I am looking at a possible failure mechanism where the edge of the footing breaks off at a 45 degree angle from the face of the existing pier col. to the outside face of the footing (nothing in AASHTO manual seems to address this condition).
Is this something I will need to drill and add steel bars for? Somehow it feels like I am creating a problem out of nothing. The 45 degree shear face has some Vc, but not enough (Vc=.95(4000psi)*1/2. It is appearing like I have to add almost 15 1.5" 150 ksi dywidag bars vertically into the footing to add resistance.If I do this on all six piers under all bearings I will have to drill 180 holes.
The footing is unreinforced except for a couple horizontal bars just above the piles. the footing is 14.5 x 14.5 feet, 6 feet thick with a 7x7 foot pier column (at base). My temporary columns are 7 x 3.75 feet in outline and extend to the edge of the footing between the pier and the footing edge (both sides of column) and support 1,700 kips (DL and LL with 50% markup).
Does anyone have any comments or experience with this sort of thing?
At the bottom of the columns I am bearing on the old pier footing. My temporary columns are made up of four ibeams with bearing plates. AASHTO bearing pressure loads are just within limits, but I am analysing the footing for the excentric loads of the temp jacking columns.
The existing footing is on piles with the pier pedestal in the center and is six feet thick. It looks like it's designed correctly. My temporary jacking structures are located outboard of the pier column and extend to the edge of the footing. I am looking at a possible failure mechanism where the edge of the footing breaks off at a 45 degree angle from the face of the existing pier col. to the outside face of the footing (nothing in AASHTO manual seems to address this condition).
Is this something I will need to drill and add steel bars for? Somehow it feels like I am creating a problem out of nothing. The 45 degree shear face has some Vc, but not enough (Vc=.95(4000psi)*1/2. It is appearing like I have to add almost 15 1.5" 150 ksi dywidag bars vertically into the footing to add resistance.If I do this on all six piers under all bearings I will have to drill 180 holes.
The footing is unreinforced except for a couple horizontal bars just above the piles. the footing is 14.5 x 14.5 feet, 6 feet thick with a 7x7 foot pier column (at base). My temporary columns are 7 x 3.75 feet in outline and extend to the edge of the footing between the pier and the footing edge (both sides of column) and support 1,700 kips (DL and LL with 50% markup).
Does anyone have any comments or experience with this sort of thing?