I have several questions and would like to hear from experts here.
Given:
ASCE 74 states, in Appendix J Section J.4, the Broken Wire Load (BWL) is equal to the everyday bare wire tension (EDT) of the ground wire and about 70% EDT of a conductor. It also says in the next paragraph, the single BWL, applied as a static bare wire load in no wind/ice conditions has proven adequate for protection after a wire breaks in all conditions except for breakage under heavy ice conditions or where the supports were relatively brittle.
Questions:
#1) If I have a continuous ground wire at the top of a tower and (2) power cables at a cross arm, should I assume that the wires to be broken would be the ground wire and just one power cable? The remaining intact wire would exert vertical/radial loads; should I estimate those vertical/radial loads of the intact wire in a 60 deg F normal condition with no wind and no ice? Section 3.1.2.1 says "the other support points all carry full bare wire vertical loads with no wind"; so my interpretation is, ASCE 74 suggests wire break in a 60 deg normal condition only. Why? Is it an overkill to consider wire break happenning in NESC Heavy ice loading condition (or in Extreme wind)? Sectoin 3.1.2.1 says in the end, "utilities in areas of known severe icing may consider an RSL calculated at some iced condition," and from this sentence, I think I may have to consider wire break in NESC Heavy ice.. [I'm in NYC.]
#2) My guess is, those ground wire and a power cable that are assumed to be broken would still have vertical/radial loads from the other side; is this a correct assumption? If so, for those vertical/radial loads estimation, should I assume the horizontal tension in a 60 deg normal condition only? [back to Question 1]
#3) If the two power cables are supported by a cross arm, one on each side of the pole, assuming one cable broken would create torsion. Then, cross-arm and the pole shall be designed for this torsion? [I'm just a structural engineer..]
#4) If the wire support is of a suspension-type, which gives flexibility, BWL would be as explained in Section J.4, right? Section 3.1.2.1 mentions Risidual Static Load (RSL), and it sounds like RSL means the same thing in BWL described in Sect.J.4; am I right or wrong?
#5) How about the wire attachment that is of the dead-end type, i.e. terminations at thru vang? Wire tensions may be different depending on the span/installation tension, etc.. In this case, is the concept of wire break even applicable? If so, BWL should be estimated differently? What if those power cables are carried by EHS messenger?
#6) What if I have a cont. GW at the top and (4) power cables instead of two? Still assume one GW and one conductor broken? Sect.3.1.2.1 Method 1 states, apply RSLs to a nominal one-third of the conductor support points or to one ground wire support point, or both. Does that mean I need to assume one GW and at least two conductors broken? What is the difference between a single-circuit line and double-circuit lines? [probably a dumb question from someone who has little electrical background..]
Any input would be greatly appreciated.
Given:
ASCE 74 states, in Appendix J Section J.4, the Broken Wire Load (BWL) is equal to the everyday bare wire tension (EDT) of the ground wire and about 70% EDT of a conductor. It also says in the next paragraph, the single BWL, applied as a static bare wire load in no wind/ice conditions has proven adequate for protection after a wire breaks in all conditions except for breakage under heavy ice conditions or where the supports were relatively brittle.
Questions:
#1) If I have a continuous ground wire at the top of a tower and (2) power cables at a cross arm, should I assume that the wires to be broken would be the ground wire and just one power cable? The remaining intact wire would exert vertical/radial loads; should I estimate those vertical/radial loads of the intact wire in a 60 deg F normal condition with no wind and no ice? Section 3.1.2.1 says "the other support points all carry full bare wire vertical loads with no wind"; so my interpretation is, ASCE 74 suggests wire break in a 60 deg normal condition only. Why? Is it an overkill to consider wire break happenning in NESC Heavy ice loading condition (or in Extreme wind)? Sectoin 3.1.2.1 says in the end, "utilities in areas of known severe icing may consider an RSL calculated at some iced condition," and from this sentence, I think I may have to consider wire break in NESC Heavy ice.. [I'm in NYC.]
#2) My guess is, those ground wire and a power cable that are assumed to be broken would still have vertical/radial loads from the other side; is this a correct assumption? If so, for those vertical/radial loads estimation, should I assume the horizontal tension in a 60 deg normal condition only? [back to Question 1]
#3) If the two power cables are supported by a cross arm, one on each side of the pole, assuming one cable broken would create torsion. Then, cross-arm and the pole shall be designed for this torsion? [I'm just a structural engineer..]
#4) If the wire support is of a suspension-type, which gives flexibility, BWL would be as explained in Section J.4, right? Section 3.1.2.1 mentions Risidual Static Load (RSL), and it sounds like RSL means the same thing in BWL described in Sect.J.4; am I right or wrong?
#5) How about the wire attachment that is of the dead-end type, i.e. terminations at thru vang? Wire tensions may be different depending on the span/installation tension, etc.. In this case, is the concept of wire break even applicable? If so, BWL should be estimated differently? What if those power cables are carried by EHS messenger?
#6) What if I have a cont. GW at the top and (4) power cables instead of two? Still assume one GW and one conductor broken? Sect.3.1.2.1 Method 1 states, apply RSLs to a nominal one-third of the conductor support points or to one ground wire support point, or both. Does that mean I need to assume one GW and at least two conductors broken? What is the difference between a single-circuit line and double-circuit lines? [probably a dumb question from someone who has little electrical background..]
Any input would be greatly appreciated.